2011Code states in 210.8(B)(2) it requires all 15 and 20 amp, 125 volt receptacles in non-dwelling kitchens to be GFCI protected whether or not they are on the counter top or not.
The 6' rule no longer applies.
The only way out, is to look at whether your break room is by definition a kitchen or not. Meaning does it have both a sink and permanent provision for cooking. Odds are probably yes (sink and microwave). So no way out.
I don't believe a cord-and-plug-connected, countertop microwave qualifies as a permanent provision for cooking....
The only way out, is to look at whether your break room is by definition a kitchen or not. Meaning does it have both a sink and permanent provision for cooking. Odds are probably yes (sink and microwave). So no way out.
Microwaves may not be present at time of final inspection, do you mean that all break rooms with sinks and counter tops must have receptacles to be GFCI?Here inspectors require GFCIs in employee break rooms even with counter microwaves.
Microwaves may not be present at time of final inspection, do you mean that all break rooms with sinks and counter tops must have receptacles to be GFCI?
When you say "inspectors require" is that because of their interpretation of NEC or due to local code?
In the jobs I have done with employee break rooms they expected GFCIs.
I could point out a counter microwave is not permanent and they could point out neither is a mounted one. Both will breakdown and be replaced.
So what do you call your statement as permanent means anything used in place over 90 days, if not an interpretation? Code does not make such a distinction.Just trying to deseminate the language in code not trying to apply interpretation.