If the grounded conductor is in contact with the EGC downstream of a GFCI receptacle, with no loads on, will the GFCI trip? Downstream is all load side of GFCI.
What if the EGC was not on the GFCI grounding screw?
That is what I thought. Now the question, if the EGC is not connected at the GFCI, how does the GFCI know there is a neutral to ground fault downstream?The internal GFCI circuitry will have no connection to the grounding screw, and the GFCI function is totally independent of it.
I think the only thing electrically connected to the grounding screw is the yoke of the device that's used for mounting it to a box.
That is what I thought. Now the question, if the EGC is not connected at the GFCI, how does the GFCI know there is a neutral to ground fault downstream?
What about with no load?I believe that various techniques for neutral to ground fault detection are used. I remember that one method has a separate toroid through which all the circuit conductors pass though, and its windings are driven with a small signal at a higher frequency than 60 Hz. And so it's a little transformer where the branch circuit wires are the secondary of the transformer. If there's a neutral to ground fault downstream, there will be a closed circuit on the secondary of this transformer and so a signal current will flow on the neutral conductor. The other toroid used for detecting ground faults will then sense this current and cause the GFCI to trip.
Yes.If the grounded conductor is in contact with the EGC downstream of a GFCI receptacle, with no loads on, will the GFCI trip? Downstream is all load side of GFCI.
What about with no load?
Yeah, that cleared it right up for me!Link to GFCI controller chip. There is a description of the function of the grounded neutral detection in this datasheet. Not that I understand any of it![]()
![]()