Gfci readily accessible?

Status
Not open for further replies.
2014 Nec 210.8 gfci is supposed to be readily accessible. I saw this job where a drinking fountain is installed without the gfci readily accessible. I was told that technically 422.52 does not require it. Is this true ? I know thos is splitting hairs but i believe the intent was for the monthly test of the gfci. So doesn't the requirement apply to 422.52
 
K. Soon after i posted that question i found my answer. 422.5 makes the drinking fountain gfci required to be readily accessible.


That is correct-- The provisions of 210.8 do not apply however since 422.5- which is new to 2014 NEC- requires the gfci to be readily accessible for appliances in this section then it must be readily accessible for the drinking fountain.
 