DanZ said:
Don't forget the exceptions! :roll:

(Yes, I know, they're part of 210.8, but I had to tell an electrical examiner about the patient care area exception)

If he read 210.8 he would see the exceptions. :rolleyes:

See 517.21 also

Roger
 
roger said:
If he read 210.8 he would see the exceptions. :rolleyes:

See 517.21 also

Roger
Yeah, I know. But you have to turn the page to get to Exception number 2 to (5)!:grin:

I don't think the inspector / examiner had fully read the 08 NEC yet, and medical usually isn't a daily thing for them, I think.

517.21 is good, but it can be a AHJ decision as to whether or not there "in the room", or so I've heard. If you do use that, make sure those receptacles use the medical grade wiring standards. If the AHJ questions it, you can make the argument that there is an emergency call button in there, and someone could need patient care in the toilet room.
 