Went on a service call the day where the owner say they had the breaker trip a few times in the past year, this is in a bathroom.
What I did find out that bathroom was remodled within the last year buy a carpenter and he did the wiring also.
I checked all the wiring connections and really found nothing out of line other than a GFCI receptacle on a circuit that is already GFCI protected at the panel.
I removed the GFCI receptacle and put in a plain duplex figuring this "could cause" a occasional trip and was not necessary for protection of the bathroom circuit anyways.
On this 1 circuit is a bath fan , 3 lights, and 1 duplex receptacle.
I am assuming that the carpenter added the GFCI during the remodel but the homeowners don't remember if he added it or not, they called him and he can't remember either, all they know is that GFCI breaker has tripped since he has done the remodel work last year .
Any thoughts from you guys ??