GFCI recepatcle readily accessible

Status
Not open for further replies.

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
My reading of the article 100 definition of readily accessible tells me that such a receptacle location is readily accessible. I don't consider a door to be an "obstacle," in the sense of that article. There is nothing in the definition saying that if you have to bends down or get on your knees, it is no longer readily accessible.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I agree with Charlie opening the cabinet door or opening the door on a panel to test the GFCI isn't really different.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
IMO, that does not fit the definition of readily accessible unless the cabinet is empty. You may have to move things to get to it. I think the intent was so that home owner would use the test button but I doubt they will. Heck I never did on my house for 15 years or so.. never had a problem with them.

Accessible, Readily (Readily Accessible). Capable of being
reached quickly for operation, renewal, or inspections
without requiring those to whom ready access is requisite
to actions such as to use tools, to climb over or remove
obstacles, or to resort to portable ladders, and so forth.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
IMO, that does not fit the definition of readily accessible unless the cabinet is empty. You may have to move things to get to it. I think the intent was so that home owner would use the test button but I doubt they will. Heck I never did on my house for 15 years or so.. never had a problem with them.

Technically the definition says remove not move an object to the side to access the test button. :)

But as you say if the cabinet is empty then the point is moot.
 

jumper

Senior Member
My reading of the article 100 definition of readily accessible tells me that such a receptacle location is readily accessible. I don't consider a door to be an "obstacle," in the sense of that article. There is nothing in the definition saying that if you have to bends down or get on your knees, it is no longer readily accessible.

I agree with Charlie opening the cabinet door or opening the door on a panel to test the GFCI isn't really different.

Ditto.:happyyes:
 