We design and fabricate industrial control enclosures for PLC systems including motor control etc. We often install a 120vac outlet for use by technician when he needs to plug in his laptop and go online with the PLC for program changes. For years this outlet has just been a standard 120vac outlet. But I've started running into more requirments to have panels UL approved. I find UL 508 section 28.6.6 states the 120vac outlet must be GFCI protected if installed in a nema 3R enclosure or other enclosure intended for outdoor use. Many of my peers are going one step further to consider a washdown area within and indoor facility (typically a nema 4x enclsore) should also utilize a GFCI protected outlet.
My peers tell me 2005 NEC also supporst this requirement and may even exceed UL's requirement. But I'm having a little trouble finding which article in NEC covers this. Can someone point me in the right direction please?