H Hendrix Senior Member Location New England Dec 16, 2008 #1 Should the test button still work on this ungrounded circuit?
raider1 Senior Member Staff member Location Logan, Utah Dec 16, 2008 #2 Yes, the test button on the GFCI device does not rely on an EGC to operate. Chris
H Hendrix Senior Member Location New England Dec 16, 2008 #3 raider1 said: Yes, the test button on the GFCI device does not rely on an EGC to operate. Chris Click to expand... thanks again
raider1 said: Yes, the test button on the GFCI device does not rely on an EGC to operate. Chris Click to expand... thanks again
raider1 Senior Member Staff member Location Logan, Utah Dec 16, 2008 #4 Hendrix said: thanks again Click to expand... Your welcome again. Chris
D dcspector Senior Member Location Burke, Virginia Dec 16, 2008 #5 Just to add a gfci receptacle monitors the current flow ( via a differential transformer in the device) between the ungrounded and grounded conductors.
Just to add a gfci receptacle monitors the current flow ( via a differential transformer in the device) between the ungrounded and grounded conductors.