First receptacle in branch circuit of GFCI then other receptacle downstream need GFCI? I cannot find this in NEC 2014 anywhere
All gfci receptacles or gfci breakers will protect all downstream receptacles if you connect the load to the load on the receptacle. I am not certain what you are asking.
General GFCI requirements are in 210.8Code section
There isn't a code section the afci or gfci are designed to protect downstream loads. The code just states which outlets need protection. You can accomplish it anyway you want
If the outgoing leads from the GFCI receptacle location are connected to it's "load terminals" then all the downstream receptacles are also protected.Alright so let’s say receptacles are wired as shown and first one is GFCI would it protect downstream or I need downstream to be GFCI as well?
Sent from my iPhone using Tapatalk
Either is acceptable. It is a design issue not a code issue.Alright so let’s say receptacles are wired as shown and first one is GFCI would it protect downstream or I need downstream to be GFCI as well?