I am a little unclear of why it is acceptable to share a neutral between a circuit that has GFCI receptacles on the load and a circuit that has normal receptacles. For example, in a kitchen, there is a duplex receptacle for a gas cooktop and (3) GFCI duplex receptacles serving countertop. If the cooktop is on circuit #17 and the GFCI convenience receptacles are on circuit #19, is it ok to run a homerun consisting of circuits 17,19,one neutral, one ground? The homerun into the cooktop receptacle box and then circuit 19,the shared neutral and ground over to feed the GFCI receptacles. I have heard two different stories of how this isn't right and how it is just fine. Can someone explain why this is or isn't acceptable?
Also, what is the difference if a GFCI breaker was used for the receptacles? Why would you not share a neutral?
I have designed shared neutrals for GFCI receptacles for some time now and separate neutrals for GFCI breakers but I don't understand the explanation..
Thanks,
------------------
David-St. Louis
Also, what is the difference if a GFCI breaker was used for the receptacles? Why would you not share a neutral?
I have designed shared neutrals for GFCI receptacles for some time now and separate neutrals for GFCI breakers but I don't understand the explanation..
Thanks,
------------------
David-St. Louis