Would it be code compliant to put a GFCI receptacle on a street light @ 150" AFG ?
Would it be code compliant to put a GFCI receptacle on a street light @ 150" AFG ?
No, it's required to be readily accessible.
Yes. 210.8 New that code cycle.In 2014. But was it in 2011?
Yes. 210.8 New that code cycle.
2011 NEC
210.8 Ground-Fault Circuit-Interrupter Protection for Personnel. Ground-fault circuit-interruption for personnel shall be provided as required in 210.8(A) through (C). The ground-fault circuit-interrupter shall be installed in a readily accessible location.
Why would you think it wouldn't be. It's a receptical exposed to water for some sort of device that will be attached to the pole at which a person at ground level could come in contact with the pole.
That is how I see it as well, if the GFCI protection is required by 210.8(A) thru (C) then the GFCI device must be readily accessible. If GFCI protection is not required by 210.8 (A) thru (C) the accessibility of the device doesn't matter. So question is does 210.8 (A) thru (C) apply to OP's GFCI?Yes. The "accessibility" part is a blanket statement for all the installations of GFCIs in 210.8.
FDOT requires GFI for xmas lighting on street lights for the reason posted above..
What about the exception for GFCI receptacles on rooftops that don't meet the definition of readily accessible?
if 12 ft AGL, who ever is plugging into would be in a bucket truck. Sounds like a proposal for the 2020 NEC