mr horsepower
Member
i was doing some reading on another electrical site and came across something in an article that didn't seem correct to me.
the article -
http://ecmweb.com/grounding/electric_case_floating_dock/
what didn't seem correct -
"A ground wire provides a safe return path to ground for any leakage or fault voltages. An internal motor short would result in tripping the circuit breaker, or leakage imbalance would trip the GFCI circuit. However, with the ground wire severed at the house, electricity could not flow on this wire. Therefore, there would not be a GFCI sensed voltage imbalance at the lift motor to trip the unit. Both GFCI circuits were on the up side of where the short to ground was located. Effectively, this said the GFCI became unusable as soon as the ground wire became severed."
my question -
if i understand GFCI's correctly, they don't require a ground path to function as they operate/trip by sensing a current imbalance between the hot and neutral. so........
- how was the broken ground at the house responsible for not allowing the GFCI protected circuit(s) to not function properly?
- how could the current flow to the lake, and therefor not be seen on the neutral side, and not trip the GFCI?
.
the article -
http://ecmweb.com/grounding/electric_case_floating_dock/
what didn't seem correct -
"A ground wire provides a safe return path to ground for any leakage or fault voltages. An internal motor short would result in tripping the circuit breaker, or leakage imbalance would trip the GFCI circuit. However, with the ground wire severed at the house, electricity could not flow on this wire. Therefore, there would not be a GFCI sensed voltage imbalance at the lift motor to trip the unit. Both GFCI circuits were on the up side of where the short to ground was located. Effectively, this said the GFCI became unusable as soon as the ground wire became severed."
my question -
if i understand GFCI's correctly, they don't require a ground path to function as they operate/trip by sensing a current imbalance between the hot and neutral. so........
- how was the broken ground at the house responsible for not allowing the GFCI protected circuit(s) to not function properly?
- how could the current flow to the lake, and therefor not be seen on the neutral side, and not trip the GFCI?
.