We have a machine with a large metal casting head heated by multiple groups of heating element cartridges. The heaters are 240V/500W metallic types with a stainless 5-foot flexible conduit attached to protect the two wires back to the heating source. The heaters are periodically removed to facilitate cleaning. Although power is to be removed when the heaters are out of their receptacles, it is possible for someone to make a mistake. To better protect against electrical shock, we are replacing the heaters with types from the manufacturer that have a dedicated ground wire bonded to the metallic case.
We also want to improved the convoluted power distribution scheme in this machine and centrally locate all related components in a new enclosure. Circuit breakers, SSRs, disconnect, fuses and pilot lamps would all be in one box. The existing design utilizes dedicate 2-pole GFCI breakers for each heater group. With grounded heaters, I no longer see a requirement for the GFCI type breaker. My plan is to use standard DIN rail 2-pole breakers.
I don?t want to endanger anyone with my preferences or violate an accepted practice or regulation. Does the NEC address this issue?
We also want to improved the convoluted power distribution scheme in this machine and centrally locate all related components in a new enclosure. Circuit breakers, SSRs, disconnect, fuses and pilot lamps would all be in one box. The existing design utilizes dedicate 2-pole GFCI breakers for each heater group. With grounded heaters, I no longer see a requirement for the GFCI type breaker. My plan is to use standard DIN rail 2-pole breakers.
I don?t want to endanger anyone with my preferences or violate an accepted practice or regulation. Does the NEC address this issue?