GFCI Required?

Status
Not open for further replies.

Samz

Member
I have had different answers on this question. If I install receptacles under the overhang of a house for Christmas lighting do they have to be GFCI protected. I read the exception to 210.8 (A)3 I just don't understand if the circuit has to not be readily accessible AND supplied by a dedicated branch circuit for snow melting and deicing equipment, or if it could be either. :(
 
Re: GFCI Required?

Since it's not dedicated for snow melting it does need GFCI protection. I wouldn't even think of doing it any other way.
 
Re: GFCI Required?

The key word is "and". If the dedicated snow-melting circuit has a receptacle that is readily accessible, it needs a GFCI. If it's not, you don't need one. In this case, it doesn't matter since you are using it for lighting.

It must have GFCI protection.

[ November 15, 2005, 10:30 PM: Message edited by: jeff43222 ]
 
Re: GFCI Required?

The NEC in 210.8 has no exceptions that exempt the requirement.
As an inspector, I would answer "in the interest of safety, use a GFCI, it's cheap insurance, the life you save may be your own or someone dear to you!
 
Re: GFCI Required?

On a side note, most of the snow melt and de-icing cable I have installed have installation instructions that require equipment rated ground fault protection.

Chris
 