Gfci required

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have sewage sump pump receptacle in indoor wet location. I said to provide gfci since NEC 2017 Article 210.7(b) says so. However, engineer came back saying gfci not required per NEC 2017 Article 620.85. Does NEC 2017 Article 620.85 override NEC 3017 Article 210.8(b) and gfci would not be required or is the gfci required?


Sent from my iPhone using Tapatalk
 
I have sewage sump pump receptacle in indoor wet location. I said to provide gfci since NEC 2017 Article 210.7(b) says so. However, engineer came back saying gfci not required per NEC 2017 Article 620.85. Does NEC 2017 Article 620.85 override NEC 3017 Article 210.8(b)
Yes it overrides it, but the sump pump needs to be a single receptacle.
 
I have sewage sump pump receptacle in indoor wet location. I said to provide gfci since NEC 2017 Article 210.7(b) says so. However, engineer came back saying gfci not required per NEC 2017 Article 620.85. Does NEC 2017 Article 620.85 override NEC 3017 Article 210.8(b) and gfci would not be required or is the gfci required?


Sent from my iPhone using Tapatalk
620 is Elevators. Is that your location?
 
If the location requires the receptacle to have GFCI protection then it needs the protection. Is it in an elevator pit? What code section would require a single receptacle?
 