GFCI requirement
Jimbo817
New member
Des Moines, IA
The NEC states that GFCI protection is required in unfinished areas of a basement. I was wondering if this would include a family room that has an epoxy coating on a bare concrete floor. Has anyone else encountered this situation?
Dennis Alwon
Chapel Hill, NC
Electrical Contractor
If it is a family room then I suspect it is finished. The finish on the wall does not decide whether the room is finished or not
btw, welcome to the fporum
Jraef
Electrical Engineer
Your answer is in 210.8.A.5 (of the 2014 code)
(5) Unfinished basements - for purposes of this section,
unfinished basements are defined as portions or areas
of the basement not intended as habitable rooms and
limited to storage areas, work areas, and the like
Little Bill
Tennessee NEC:2017
As of the current code, any room that is finished to a habitable state in an otherwise unfinished basement, would not require GFCI protection even with a concrete floor. As I understand it, the 2020 (or maybe later) code would require all basements to have GFCI protection.