GFCI requirements for residential kitchen and hydrotub

Status
Not open for further replies.

chitt

Member
Are all outlets located on the walls above a residential kitchen countertop required to have GFCI protection (regardless of the distance from the sink)?
Is the requirement for GFCI protection for a Hydrotub a new requirement (my tub was installed in 1993, and I'm not sure if it has one)?

Thanks in advance for your response.
 

chitt

Member
Re: GFCI requirements for residential kitchen and hydrotub

Additional questions regarding GFCI -

If all the outlets above the residential countertop are required to be GFCI protected, was this a requirement in 1993?

Was there a GFCI protection requirement for hydratubs in 1993?

If these questions have been answered previously, I apologize for not being able to find them - I did search for this information but was unsuccessful (this is my first time to use this website).

I appreciate any help or answers I can get.
Thanks.
 

russ

Senior Member
Location
Burbank IL
Re: GFCI requirements for residential kitchen and hydrotub

GFCI.

1981 NEC tub motors.
1987 NEC required receptacles serving kitchen sinks.
1996 NEC receptacles serving all kitchen counters.

Russ
 

luke warmwater

Senior Member
Re: GFCI requirements for residential kitchen and hydrotub

1993 NEC:
210-8(5) required GFCI within 6' of kitchen or wetbar sink
680-70 required GFCI protection for hydromassage bathtubs
 

chitt

Member
Re: GFCI requirements for residential kitchen and hydrotub

This is exactly what I needed to know. Many thanks to all who responded.

Sincerely,

CHitt
 