1 of 2 side-by-side water fountains installed outdoors were removed from service, now exposing a non-GFCI outlet.
The NEC did not require a GFCI outlet with the water fountain installed (cord and plug inaccessible).
Where as custodial services frequently use this, "new outlet" for vacuums and blowers, etc., I suggested a GFCI should now be installed, as the outlet is outdoors, accessible, within 6 ft. and very damp environment (approximately a foot away from adjacent fountain, and angle stop for same), and should also be protected with a receptacle cover.
The circuit breaker is not a GFCI. If anything at all, circuit should be least locked out/tagged out until water fountain is replaced.
A GFCI outlet doesn't cost that much! I think this is common sense. Just can't find the supporting code requirement. Any suggestions? Thank you.
The NEC did not require a GFCI outlet with the water fountain installed (cord and plug inaccessible).
Where as custodial services frequently use this, "new outlet" for vacuums and blowers, etc., I suggested a GFCI should now be installed, as the outlet is outdoors, accessible, within 6 ft. and very damp environment (approximately a foot away from adjacent fountain, and angle stop for same), and should also be protected with a receptacle cover.