GFCI requirements

Status
Not open for further replies.

gmayeux

Member
i have installed a tankless water heater underneath a pedestal lavatory, it is 20 amp 240 volt 3 wire, cord and plug connected, the inspector is mandating that it be GFCI protected,
what would be the best way to accomplish this. i can put a GFCI breaker but would this mean running a neutral and if so what would it connect to .
 

iwire

Moderator
Staff member
Location
Massachusetts
You should ask the inspector for a code reference, the NEC does not require this to be on a GFCI.

If you decide to put one in then all you need to do is buy a two pole GFCI. You will not have to run a neutral to the load but you will have to connect the neutral from the breaker to the panel neutral bar.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
gmayeux said:
. . . the inspector is mandating that it be GFCI protected. . . .
Based on what? 210.8 only requires GFCI protection for 125 volt outlets, and I didn't see anything in 422 (Appliances) that talked about GFCI. Unless there is some related local requirements (and if there is, you should be able to ask for a specific citation), I would say that this inspector is making up rules, and does not have the authority to do so.
 