Hello,
I re-fed a spa disconnect today,
I'm not sure of the make, but I was on my belly, it's in an awkward spot, I started getting rained on and I needed to get out of there to pick up the mrs.
So I was unable to figure it out.
I turned on the breaker at the panel. Checked for voltage at the disconnect and then the 240v pump receptacle and 120v receptacle. All good.
Check hot to ground on both the 120v receptacle and the 240v receptacle. It did trip the gfci in the enclosure that goes to the contactor.
How did it trip when I tested the 240v leg to ground?
I google and was able to find this (sure looks like the unit), but can't find the schematic.
The exterior is what it looked like with the cover closed, but if you opened the door it looked like the guts in the picture I supplied.
The disconnect is pull out.
May I add, Is this permissible for a pool pump? A 240v circuit feed through a contactor fed from a 120v gfci (again I don't know how it works if thats what it's doing)
Thank you.
I re-fed a spa disconnect today,
I'm not sure of the make, but I was on my belly, it's in an awkward spot, I started getting rained on and I needed to get out of there to pick up the mrs.
So I was unable to figure it out.
I turned on the breaker at the panel. Checked for voltage at the disconnect and then the 240v pump receptacle and 120v receptacle. All good.
Check hot to ground on both the 120v receptacle and the 240v receptacle. It did trip the gfci in the enclosure that goes to the contactor.
How did it trip when I tested the 240v leg to ground?
I google and was able to find this (sure looks like the unit), but can't find the schematic.
The exterior is what it looked like with the cover closed, but if you opened the door it looked like the guts in the picture I supplied.
The disconnect is pull out.
May I add, Is this permissible for a pool pump? A 240v circuit feed through a contactor fed from a 120v gfci (again I don't know how it works if thats what it's doing)
Thank you.