Setting up a test station at a bench in a lab. Powering it with cord & plug connected to a GFCI receptacle about one foot away.
Time for a safety test.
Green light is on at GFCI receptacle. Press test button and voltage goes to zero, green light goes off, button pops out. Press reset button and green light comes back on. So far so good.
Place jumper at test station from hot to neutral. Insert plug in GFCI receptacle to power the test station. Breaker trips in the panel. GFCI does not trip. Not good.
Reset breaker. Use GFCI tester and it successfully trips the GFCI.
Try another test so there is no short at power up unlike the first unfavorable test. Took a probe with an alligator clip and clipped it to the neutral at the test station. Insert plug in GFCI receptacle to power the test station. Take other end of probe and swipe the hot. Blue sparks & welding in action; breaker trips. GFCI never tripped. Not good.
There is no way someone can safely work on this test station. It will not be used in this condition. These test results are telling me that if someone touches both hot & neutral, they are subject to the 20A breaker and will be afforded zero protection from the GFCI.
What's going on?
Time for a safety test.
Green light is on at GFCI receptacle. Press test button and voltage goes to zero, green light goes off, button pops out. Press reset button and green light comes back on. So far so good.
Place jumper at test station from hot to neutral. Insert plug in GFCI receptacle to power the test station. Breaker trips in the panel. GFCI does not trip. Not good.
Reset breaker. Use GFCI tester and it successfully trips the GFCI.
Try another test so there is no short at power up unlike the first unfavorable test. Took a probe with an alligator clip and clipped it to the neutral at the test station. Insert plug in GFCI receptacle to power the test station. Take other end of probe and swipe the hot. Blue sparks & welding in action; breaker trips. GFCI never tripped. Not good.
There is no way someone can safely work on this test station. It will not be used in this condition. These test results are telling me that if someone touches both hot & neutral, they are subject to the 20A breaker and will be afforded zero protection from the GFCI.
What's going on?