A customer has a 10/3 uf cable from house to boat dock on a lake that has 2-20A 1p circuits. Can you use a
2p20A Gfci breaker for these two circuits for protection to the boat dock.
10/3 would mean 2 conductors and a ground in rubber cord. For some reason rubber cord is labeled that way while nm, uf, etc all ignore the equipment grounding conductor when labellingby a 10/3 UF cable do you mean 3 conductors and a ground? or 2 conductors and a ground?
Not really sure if its UF are not i do know it has black, Red, white , and green . Thats why i was wanting to see if i could i use a 2p 20A Gfci breaker to protect the two circuits.
Would an isolation transformer or galvanic isolator on the boat work and cost less,?I would be cautious here. Not sure why you are installing a gfci on the feeder unless this dock qualifies under art. 553. If you use a standard gfci my guess if that you may have issues with it tripping-- depending on what you are feeding. I have a customer that has a boat that will not run on a 4-6ma nor a 30 ma gfci. He needs a 100 ma gfci which will cost a $1000 or so. If you are just feeding lights and a receptacle you may be fine
Would an isolation transformer or galvanic isolator on the boat work and cost less,?
Is 10/3 UF anything other than flat, grey cable? Serious question as I dont think Ive ever seen smaller gauge UF any other way.
I would be cautious here. Not sure why you are installing a gfci on the feeder unless this dock qualifies under art. 553. If you use a standard gfci my guess if that you may have issues with it tripping-- depending on what you are feeding. I have a customer that has a boat that will not run on a 4-6ma nor a 30 ma gfci. He needs a 100 ma gfci which will cost a $1000 or so. If you are just feeding lights and a receptacle you may be fine
why would a gfci a issue on a feeder ? a 100ma gfci to protect what ?