KansasSparky
Member
- Location
- Newton, Kansas
I went on a service call with my supervisor to a dental office. They have two sterilizers plugged into the same circuit along with some other small machines, the problem is that they are tripping the gfci that they are plugged into. We put a clamp meter on the circuit and it is pulling 22 amps. We separated the circuit and added another gfci because my supervisor thought that the gfci was acting as a breaker and tripping. We got called out again because they are still tripping but only one of the sterilizers is tripping the gfci?s. Both are brand new gfci?s and the sterilizers pull 9 amps a piece. My thought is that the sterilizer is leaking current which is what is tripping the gfci. Is there anyway to test the machine to check this? And we can't put in a regular duplex because it is within 6 ft of a sink.