powerplay
Senior Member
- Location
- In front of a computer.
In Canada in an old house with new NMD90 14/2 garage wiring connecting to receptacles and bathroom lights without the third bare "bond/ground", I've intercepted the cable from the panel with an GFCI receptacle to protect the ceiling fan with no bare "bond" reference to ground through pipe. The gfci simply does not reset. If the old wiring without a ground reference (outside the white common) is shorting out it would really have no where to go to trip the gfci that I can see? I checked visible connections, and although some sloppy connection to devices where made, the taped soldered parallel connections appeared ok. I am considering a possibility that the conductors insulation from stiff cables shoved into existing gfci receptacles crammed into ungrounded metal boxes are damaged at the metal connector, but really have no where to go to be able to trip the gfci? The same in another location... The original Siemens circuit breaker that is drawing no power did not trip when the gfci was taken out of the circuit... Could the gfci be too sensitive to some odd load?