pfactor2
Member
- Location
- United States
Curious if anyone has run into this issue. On a routine private inspection required by insurance company, the report noted the need for GFCI's pool pump motors on the property. One in particular ran fine for a week then would trip immediately. The existing system, from approximately 35yrs ago, had one liquid tight NM conduit with both the motor 208V 1/P and chemical feeder 120V circuits ran to a 3P relay box. I first did a megger check on the motor and it was borderline bad. Temporarily ran 12/2 Romex directly from the vac-pac panel to the line of relay essentially separating the the motor and chemical feeder circuits in separate runs. After this the GFCI did not trip, could I assume inductance was the culprit in this tripping problem? BTW
they elected to install a new motor since the existing was 5yrs old and they run 24/7/366 this year HA!
they elected to install a new motor since the existing was 5yrs old and they run 24/7/366 this year HA!