GFCI tripping problem
sparrott4
A little help please. A contractor replaced a 120v outdoor luminaire with a 12v luminaire. A small electronic transformer was installed at the luminaire to make the conversion. Everything is listed for the purpose.
The problem is that when power is applied to the line, it trips the GFCI breaker (outdoor rated receptacle). All connections seem good, the transformer was replaced and the GFCI was replaced - still the breaker trips.
I don't know if it matters but the transformer does not have a ground wire (plastic enclosure). The ground wire to the transformer location was taped off. The luminaire is an MR-16 type and has no connection to ground.
I spoke with the transformer manufacturer and he couldn't think of any reason for this aside from the possibility that there might be a nick in either the 120v or 12v wires. He also mentioned that electronic transformers might lose some voltage due to capacitance passed over to the secondary side of the transformer (don't understand that).
Can anyone think of a possible cause for the GFCI to trip in this scenario (aside from a nick in the wire)?
It won't have anything to do with the low-voltage (12v) side of the transformer. GFIs cannot detect a ground fault beyond a transformer.
Does the breaker still trip with nothing plugged in?
Is it possible to tell the difference between the breaker tripping because it senses a ground fault (3-5 milliamps) and the breaker tripping because there is a short circuit (500 or more amps)? Maybe the replacement was not done well, and there is a wire with nicked insulation that would have even caused a non-GFCI breaker to trip.
I think sparrott4 has a receptacle type GFCI, not a breaker type.
Does the transformer plug into the receptacle?