GFCI Tripping

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Seemingly topic du-jour lately...
Friend called... new restaurant installation 120/240 I have not viewed the installation.
All the GFCI breakers on "B" phase are tripping...move same breaker to "A" phase and they hold.
Voltages phase to phase and phase to ground are good,
Suggestions as to cause ?
(Siemens breakers)
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
It's the "Energy Efficiency" new equipment that is responsible for it. The GFCI do not like the signature that is put out to control the speeds of the new DC speed control motors and equipment.
 

Attachments

  • TIA Log No. 1687, Final Technical Committee.pdf
    148.6 KB · Views: 3
  • Proposed_TIA_1748_NFPA_70.pdf
    1.4 MB · Views: 4

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
Listed the wrong TIA


Yes ... It's "All the GFCI breakers on B". It's a GFCI problem.
They why do they hold when moved to "A"???

There are millions of VFD;s connected to GFCI'S that work fine. Some VFD's are not compatible with GFCI's do to high frequency "noise" This is why new standards need to be made for breakers and equipment.

When GFCI's were first introduced there were appliances/utilization equipment that were not compatible. New standards had to be made for leakage current. That didn't mean nothing was comparable with GFCI's.
 