I'm a little stuck here. In laws bought a house in central Florida Lake county. Built in 06. For some reason ALL gfci's (bathrooms) all on the local circuit. And patio gfci's on local circuits. ALL trip when on that particular circuit when an exhaust fan or ceiling fan is turned off after it was turned on. If that makes sense. I know it has to do with grounding but everything seems fine. Needing some help here. Thanks
To help you trouble shoot your problem, I've some questions for you:
1) Do you have GFCI breakers or receptacles?
2) If GFCI receptacles, is there one GFCI receptacle per circuit, or multiple? What brand GFCI receptacles?
3) Are any of the affected circuits that trip, or circuits that serve the fans, multi-wire branch circuits?
4) You write "ALL trip on that particular circuit..."; is there more than one GFCI receptacle per circuit?
5) Are the fans on the circuits with the GFCIs that trip?
6) Does the ceiling fan trip the GFCI(s) when switching speeds from H-M, M-L, or just from L (Low) to Off?
GFCI trips have nothing to do with grounding and everything to do with current imbalance between ungrounded and grounded conductors.
If two different fans are causing trips when turned off, I would tend to rule out the fans as the problem.
If there are multiple GFCI devices (breakers and/or receptacles) on one circuit, I would remove the extras (the ones on the load side of the first GFCI protection device).
I would verify that all GFCI wiring is correct in regards to polarity and line/load.