RCD, not RTD. It means "Residual Current Device", formerly known as an RCCB (Residual Current Circuit Breaker) but, it may or may not have actually had the regular kind of CB trips, they don't necessarily have to. If it is actually a full on circuit breaker, then it is called an RCBO. Either way, it is
not a GFCI in the same sense that we use that term, their rules are very different. GFCI is a specific term reserved for use here in North America in describing a PERSONNEL protection system that will trip at between 4 and 6mA of ground current. This is also referred to as a Class A Ground Fault Circuit Protector. That is NOT what they will have on their main CB, it would likely never hold in. And RCD is allowed to trip at 30mA, maybe even up to 100mA depending on the system. By our rules, you would be long dead. But you cannot directly equate EU distribution system requirements to ours, they have some very different issues and rules.
The closest thing we have to that is "Equipment Ground Fault" protection, also called "GFP". There are several sub-classes within that as well, too detailed to go into, but you can read about them all
here.