bikeindy said:GFCI doesn't apply to laundry room. the sink you are thinking of is a wet bar sink.
You can also place the GFCI in another location in the laundry area, and place the washer on the load side of it. Best of both worlds. I will GFCI protect a receptacle not within the rule, just to get the reset button out from behind the washing machine.mbike01 said:When a receptacle supply a washer is within six feet of the sink does it still have to be GFCI? the washer will be hard to move if the gfci nuisance trips
Digging up an old comment:bikeindy said:you got me. I missed that change from 2002.
I never forgot that...LOLhurk27 said:...we all win when we get it right![]()
![]()
![]()
georgestolz said:You can also place the GFCI in another location in the laundry area, and place the washer on the load side of it. Best of both worlds. I will GFCI protect a receptacle not within the rule, just to get the reset button out from behind the washing machine
It never applied to this section. It appears that all of the execptions will be removed in the 2008 code.did we loose the single receptacle not readily accessible exception in 2005?
izak said:did we loose the single receptacle not readily accessible exception in 2005?
A single receptacle does not meet the code requirements in a laundry room if it is within 6' of a sink. Re-read 210.8.A(6).ronbannon said:You could either put gfi in due to sink, or a single outlet for washer. Also if
the dryer is gas using both outlets in dupex that is good so nothing else
could be pluged in. If you have 2 outlets on same circuit for washer and dryer than blank one.