can a GFCi recptacle be used in a circuit that has GFCI breaker?
Yes.can a GFCi recptacle be used in a circuit that has GFCI breaker?
can a GFCi recptacle be used in a circuit that has GFCI breaker?
Since the trip point for neither breaker nor receptacle is adjustable, I fear that if you leave the breaker in place some of the nuisance trips will still be at the breaker. It is definitely not a situation where the closest GFCI trips first.I have been tasked with installing the recptacles in a clean room and to leave the gfci brkr. My concern is of nuisance trips. The reason we are changing the outlets is for the operators in the clean to be able to reset, because the brkr panel is in a hard to access area.
Not a big deal for you, and definitely not a big deal for safety, which would be just fine.If there was an event at the end of the circuit though any on of them cold trip. But big deal.
Since the trip point for neither breaker nor receptacle is adjustable, I fear that if you leave the breaker in place some of the nuisance trips will still be at the breaker. It is definitely not a situation where the closest GFCI trips first.