Would a GFCI circuitbreaker be required for a 208 volt cord and plug connected heater,on a covered patio, if the recept is set at 8 feet? This patio is off a bar and grill. Its a 2 pole 20 amp circuit. The quartz tube heater is set at 8 feet.I dont think I need one because it is not readily accessible. Thoughts?
 
Re: GFCI

No 210.8(B) only requires 125 volt receptacles in bathrooms, rooftops, kitchens to be protected.

But it would be a good idea from a legal stance. :D
And I have no idea why the NEC doesn't require outdoor receptacles to be GFCI protected? :confused:

[ October 25, 2004, 12:45 AM: Message edited by: hurk27 ]
 
Re: GFCI

I am confused doesn't 210.8A(3) say outdoors. This says all receptacles outside have to be GFCI protected except ones that are not readily accessible. Nevermind I see it is off a bar. Must read closer.

[ October 25, 2004, 01:29 AM: Message edited by: gvmv ]
 
Re: GFCI

A GFCI protected receptacle is not required for this application, for Dwellings or Other than dwellings. 210.8(A) &(B) are for 125 volt rated receptacles.

Installing this receptacle is at the owner's/installer's discretion.

Yup! I am up pretty early this morning :D

Pierre
 