gfci
southernboys
Has anyone here tried the nikar tradename gfcis. If so have you guys experienced any problems with these gfcis. Also If I were to put a 15a gfci on a 20a breaker 12 gauge wire would this cause a gfci recep to melt. Its under no load at time of melting. I disagree with this practice however my boss at this time sees no problem in putting gfci in under these circumstances. To me it may not melt the recep but would prevent breaker from tripping. Opinions please.
Re: gfci
Melting can only be caused by heat. Heat is generated by the flow of current, usually excessive current from a possible overload or even lightning surge. My guess is a defective product or improper connections/terminations. The code permits 15A rated devices on 20A branch circuits. I don't see this being the cause of your problem
Re: gfci
Sounds like a bad g.f.c.i. Try Leviton.
Most 15 amp switches,recept can be installed on 20 amp circuit with #12 wire.
Re: gfci
I've said it before, and I'll say it again:
The ampere ratings of 15- and 20-amp receptacles refer to the slot shapes, and not (necessarily) the current capacity. There's no problem here.
The metal parts of 15- and 20-amp receptacles within a given grade are the same. That 15-amp GFCI receptacle is rated for 20 amps feed-through.
Re: gfci
I apreciate you guys quick responses. we are switching to levitron gfcis as there is obviously an internal problem with these nikar gfcis. Its just kinda scary when the whole back of the damn thing has melted. Got the point 15a is good for 20a. Thanks again
Re: gfci
Are sure about the spelling of 'nikar'??
I tried to do a search on them and couldn't find anything. That doesn't sound good.
I like the P&S brand, but at this point, Leviton sounds like a step up for you.
Re: gfci
I've gotta say, from experience, that using a brand of product that nobody's ever heard of before is a sure-fire recipie for callbacks. I don't care what it is.
Re: gfci
There has been several foreign companies that have been flooding the market with cheap GFCI's and other electrical items.
Many of these are getting into the US with boot legged UL labels on them. UL has stopped one such company and are trying to get info on more and need our help when ever we can. I have sent them samples of several GFCI's, fixtures, and other items that have made its way into our market. Progressive out of Florida was one that has turned around and started getting their GFCI's listed. But there are others.
When you get one of these drop UL a line they will love to hear from ya. Also save them a sample and they will pay all cost to have you ship it to them.