T thewizardofwatts Member Oct 4, 2004 #1 If you install a receptacle on the out side of a deck of a six story apartment building, is gfci required ? I cant find a reference to no grade access above 6-6". in 210.8 (A)3
If you install a receptacle on the out side of a deck of a six story apartment building, is gfci required ? I cant find a reference to no grade access above 6-6". in 210.8 (A)3
P pierre Senior Member Location Westchester County, New York Oct 4, 2004 #2 Re: gfci 210.8(A)(3) Outdoors Pierre [ October 04, 2004, 04:37 PM: Message edited by: pierre ]
iwire Moderator Staff member Location Massachusetts Oct 4, 2004 #3 Re: gfci Wizard if it is an outdoor dwelling unit receptacle it must be GFCI protected, grade level or the fiftieth floor balcony. Edit: Changed outlet to receptacle. [ October 04, 2004, 04:47 PM: Message edited by: iwire ]