Harley
There are tubs that do use only 220v 3-wire hookup and don't use a neutral at all matter of fact most of the ones I have seen lately are of this type, and could be from cutting cost in manufacturing as less components are needed. but a 4-wire tub does need the neutral because of components needing 120v.
In this case this is a 3-wire tub and there is no neutral they do make a breaker without the neutral terminal on it but the one that he had does have a neutral terminal so with this type of tub the neutral terminal will not have a wire terminating to it and is left blank. what he was told by the service tech was that he had to connect the grounding wire (EGC) to this neutral terminal on the breaker and not to the ground/neutral bar in the main breaker panel.
What this causes is that in the event of a hot to ground leakage at the tub the GFCI will treat it like normal current and not trip and this is a dangerous and deadly shock hazard that should not have been ever told to someone to do!!! as this EGC should always terminate on the proper grounding buss and never to a GFCI neutral terminal. Because someone could of been killed and this should also be a good lesson that this kind of equipment is not for the unqualified to be hooking up as you could kill someone and it could be someone you love very much. so if you don't understand what your working on leave it alone.
leave it for the professional.
And I don't say this because I need the work. I say this because there are many DYS, and even some pro's that can get in over their heads really quick! when it comes to electricity around water people can be killed if the installers don't know what there doing. And I don't even want to go into liability issue.
This is why we have the NEC and forums like this to help us all so that maybe we might be able to prevent another unnecessary loss of life.
Wayne