Public Comment No. 1640-NFPA 70-2018 [ Section No. 210.8 [Excluding any Sub-Sections] ]
Ground-fault circuit-interrupter protection for personnel shall be provided as required in 210.8(A) through (F). The ground-fault circuit interrupter shall be installed in a readily accessible location.
Informational Note No. 1: See 215.9 for ground-fault circuit-interrupter protection for personnel on feeders.
Informational Note No. 2: See 422.5(A) for GFCI requirements for appliances.
For the purposes of this section, when determining distance from receptacles the distance shall be measured as the shortest path the supply cord of an appliance connected to the receptacle would follow without piercing a floor, wall, ceiling, or fixed barrier, or the shortest path without passing through a
door, doorway, or window.
Statement of Problem and Substantiation for Public Comment
The consequence of this change is that receptacles in adjacent rooms will need to have GFCI protection. Such receptacles may be on a separate circuit and only require protection for that one outlet. This adds cost and more chances for enforcement against installers for an unknown benefit. In addition, Article 400.12 already prohibits cords from being run through doorways.
Committee Action: | Rejected |
Resolution: | GFCI protection is required for receptacles that are six feet or less from the potential hazard in 210.8(A) and (B), regardless of any intervening doors of any kind, or doorways of any kind. |