Marine@360
Member
- Location
- Philadelphia
- Occupation
- Electrical Designer
We utilize 440/120V, 3PH, 3W ungrounded systems on board the vessels, will a GFCI receptacle or circuit breaker function properly with (2) 60V conductors?
If vessel electrical generators operate > 60Hz, no sure if GFCI outlets are listed for it.on board the vessels, will a GFCI
If compatible GFCI devices exist for 120D/60V systems, requirements are usually adopted from ABYC regulations.will a GFCI receptacle or circuit breaker function properly with (2) 60V conductors?
Take a screenshot of the relevant sections of the diagram. You can embed most standard image formats.I would like to insert a diagram but I do not know how to insert a PDF
Yes. It won't care what or if there is a ground reference, all it will care about is having sufficient supply voltage for the electronics and then whether the current going out on one conductor is equal to the current coming in on the other.We utilize 440/120V, 3PH, 3W ungrounded systems on board the vessels, will a GFCI receptacle or circuit breaker function properly with (2) 60V conductors?