Do they require and islolated ground or seperate neutral all the time?
Do they require and islolated ground or seperate neutral all the time?
GFCIs never need any equipment grounding conductor.
.
GFCIs never need any equipment grounding conductor.
You do need a dedicated neutral on the load side of a GFCI unless it is a multipole GFCI breaker and in that case the same neutral must be used for each pole.
may I add the words "to function"
I will look again but I thought I saw on pools the GFI had to also have a EGC
My answer was directed at the GFCI.
If I asked 'Does a 100 watt A-19 lamp require a ground' what would your answer be? :smile:
"mr inspector, I-wire said it didn't need a ground"
my answer would be that your age is showing,.... CFL !
a GFCI is considered a Grounding Device by definition.
The receptacle itself does, but not the functionality of the GFCI.I will look again but I thought I saw on pools the GFI had to also have a EGC