Gfci does not use an equipment ground. It requires a seperate neutral on the load side. In other words you can run a 12-3 to the box hit the line side of one kitchen gfci then on to the line side of an other gfci outlet.
 
Do they require and islolated ground or seperate neutral all the time?

GFCIs never need any equipment grounding conductor.

You do need a dedicated neutral on the load side of a GFCI unless it is a multipole GFCI breaker and in that case the same neutral must be used for each pole.
 
Need a little more information ,A GFCI Breaker requires a dedicated neutral you can use a common ground,A GFI receptacle the hot and neutral cannot be shared on the load side but can have a common ground.
 
GFCIs never need any equipment grounding conductor.

You do need a dedicated neutral on the load side of a GFCI unless it is a multipole GFCI breaker and in that case the same neutral must be used for each pole.

I will look again but I thought I saw on pools the GFI had to also have a EGC
 
My answer was directed at the GFCI.

I just didn't want someone to take that statement literally and run with it ... "mr inspector, I-wire said it didn't need a ground" :D
If I asked 'Does a 100 watt A-19 lamp require a ground' what would your answer be? :smile:

my answer would be that your age is showing,.... CFL !
 
My thought is that if the EGC is there, hook it up. Otherwise, a GFCI is considered a Grounding Device by definition. As for pools 680.6 specifies GFCI 's are to be grounded.
 