Is it okay to install a GFCI receptacle in place of an ungrounded receptacle, the receptacle would be the first one in line from the breaker. If this is done can I replace all of the other receptacles on that circuit with regular grounded receptacles as long as I install a sticker stating that these receptacles are now GFCI protected.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Is it okay to install a GFCI receptacle in place of an ungrounded receptacle, the receptacle would be the first one in line from the breaker. If this is done can I replace all of the other receptacles on that circuit with regular grounded receptacles as long as I install a sticker stating that these receptacles are now GFCI protected.


Yes, read 406.3(D)(3)
 