I have two circuits that are sharing a neutral (single phase service). Both circuits first recep is a GFCI. When I turn one circuit on everything is fine, when I turn the second one on the GFI trips on both receps. Any ideas?
The neutral for the 2nd circuit must connect to the line side of the GFCII was thinking about that. The neutral from the panel goes to the first GfI on the line side and then all the rest of the outlets neutrals are fed from the load side of the gfi, even the next gfi. All connected with one conduit and only one neutral is pulled through the entire run. Do I need a separate neutral to feed the second gfi?
Yep. The home run neutral should split and feed each GFCI's line-side neutral terminal. Of course, the hots each land on one line-side hot terminal.The neutral from the panel goes to the first GfI on the line side and then all the rest of the outlets neutrals are fed from the load side of the gfi, even the next gfi. All connected with one conduit and only one neutral is pulled through the entire run. Do I need a separate neutral to feed the second gfi?