GFE required?

Status
Not open for further replies.

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
A cabinet I am designing has a 2500A main CB.

The vender of the CB has quoted what appears to be a GFE sensor and trip device.

I don't see any requirement in the code to have a GFE except on the feeder coming into the cabinet. Is there some benefit to putting one on the main CB for this control panel as well?
 
The load side of the feeder breaker feeds the line side of the panel disconnect? If so that would seem to be a waste of money to have them both GFP. If there are loads inbetween, then it might make sense for selective coordination.
 
Many product selectors automatically add GFP to any device >1000A when the system is 480Y/277. You have to manually deselect the option.
 
Many product selectors automatically add GFP to any device >1000A when the system is 480Y/277. You have to manually deselect the option.

That makes sense. That reminds me I need to find out from the end user just what kind of power we have there. It may not be grounded at all.

The load side of the feeder breaker feeds the line side of the panel disconnect? If so that would seem to be a waste of money to have them both GFP. If there are loads inbetween, then it might make sense for selective coordination.
As far as I know there are none.
 