I seem to remember this problem coming up before but can not find the solution, Help.
I split a 3 wire with ground cable into 2 circuits in my garage so every other outlet is a different circuit. I have two 20 amp breakers, one for the black and one for the red wire, the white wire is the common for both circuits. The white and the ground wire are on a common buss in the panel. The breakers are wired one to each side of a 240 volt service. Meaning I measure 240 volts between the red and black wires.
The problem is that one GFI will set and work OK but I can not turn the second one on. I tried putting a standard outlet on the second circuit but it will trip the first circuit GFI when I plug anything into the second circuit. Am I doing something wrong or is this not possible?
I split a 3 wire with ground cable into 2 circuits in my garage so every other outlet is a different circuit. I have two 20 amp breakers, one for the black and one for the red wire, the white wire is the common for both circuits. The white and the ground wire are on a common buss in the panel. The breakers are wired one to each side of a 240 volt service. Meaning I measure 240 volts between the red and black wires.