f i have 3 phase load with neutral however the installed GFI breaker inside panel is 3 pole only and we cant change it due to limited panel space how can we overcome this problem?
The RCBO breaker fixed at panel board is 3 pole however the load connected is 4 pole,how can overcome such problem if there is no enough space at panel board for 4 pole RCBO?
Two choices both involve installing a second "sub panel".
1. move some circuits from original panel to sub panel to make room for your breaker (if it needs more then 3 pole spaces)
2. install your breaker in the sub panel you installed.
either way you need a breaker with a connection to neutral, you can not get around that part.
3 pole with neutral GFCI is not something you generally see frequently - it may even be something you need to get that is housed in it's own enclosure.