Open Neutral
Senior Member
- Location
- Inside the Beltway
- Occupation
- Engineer
So I spec'ed a Pentair Intelliflo I2 pump. This is a variable speed 240V pump.
It keeps tripping the GFI. We tried a different GFI breaker; no joy.
So I finally called Pentair. The helpful support person asked if it was a 5ma or 6ma GFI.
Seems that line of pumps needs the latter. He mentioned the Siemens PA220GF.
He acknowledged that none of the documentation mentions that un-minor detail.
Searching for that number gets me lots of hits at swimming pool supply houses.
But this site is all SqD QO panelboards, so I have a query into SqD asking if they make
a 6ma versions. Nothing yet.
I see mention on the Siemen's site that the Siemens breaker *might* fight a SqD panel. I don't like "mights' on safety critical issues.
And here I thought GFI == 5mA.....
Sigh...