Gfi Breakers

Status
Not open for further replies.

sd4524

Senior Member
I would like to install 2 pole gfi breakers for indoor shower (waterfall pump, heat )circuits. The circuits are 20a 208v. The motors do not have a neutral connection. Will the breakers trip without any neutral. I don't think there should be any problems but just want to be sure.
 
I have hooked up 2-pole jetted/heated tubs that do not use a neutral to 2-pole GFCI breakers. Per installation instructions.
 
sd4524 said:
I would like to install 2 pole gfi breakers for indoor shower (waterfall pump, heat )circuits. The circuits are 20a 208v. The motors do not have a neutral connection. Will the breakers trip without any neutral. I don't think there should be any problems but just want to be sure.

Many hot tubs and spa units use to come with no required neutral and a GFCI was installed. It will function properly.
 