1. You do have the (correct) circuit's white on the breaker's white terminal, and the pigtail on the panel neutral bus, right? And no shared-neutral use?I am doing a temporary lighting the engineer wants the incandescent lights on a gfi ckt breaker. When you go to turn on the ckt breaker it trips instantly.
That suggests a wiring mistake. Check my #1 above.regular ckt breakers work fine no shorts three ckt breakers doing the same thing
Well gee Wally, what about the total numbers of lamps on the String?
W=AV
I am doing a temporary lighting the engineer wants the incandescent lights on a gfi ckt breaker. When you go to turn on the ckt breaker it trips instantly. Any comments would help please
thank you
Well gee Wally, what about the total numbers of lamps on the String?
W=AV
regular ckt breakers work fine no shorts three ckt breakers doing the same thing
Since it trips instantly,,,I'd be willing to bet it's not wired correctly. If it were overload, it would at least take several seconds.
I am doing a temporary lighting the engineer wants the incandescent lights on a gfi ckt breaker. When you go to turn on the ckt breaker it trips instantly. Any comments would help please
Well ok, I thought about it, I reckon... I know ... add that one extra lamp.
Dual duty GFCI - unintentional RECPT with light loads.
Some much can be left out sometimes in an OP (no offense).
Type of lamps, length of string, MWBC... Etc...
I'm going to go with a open short on the string, Rubbed open, or burnt open, which was already said.
Hey Be Safe out There!!! Happy Monday!
Aside from the obvious reasons given (short circuit, mis-wire, etc) are you using std. "A" bulbs or CFL's ? If they're CFL's that could be part or the total cause of your problem. In any case, I would start troubleshooting by unplugging the bulbs, turning on the GFCI breaker and see if the circuit holds. If it does, then start plugging in one bulb at a time and see what happens.