I ran power for a hot tube yesterday. Edit: it was a hot tub not a hot tube..........
The unit itself required 2 hots and a grnd.
The disconnect was a CH 50A 2pole GFI Nema 3R
Ran 2 hots a neutral and a grnd to the disconnect.
Ran 2 hots and a grnd to the unit.
Separate neutral (isolated) and ground ( to chassis) bars in the disconnect. Treated them as you would a sub panel ( kept them separate )
The GFI disconnect kept tripping sometimes within a few seconds and sometimes after a minute or so. Then it held and only tripped when I hit the test button.
Had the hot tub on maximum settings the whole time. ( full of cold water, so it was heating )
Current draw was 41A peak for just long enough to read it and then dropped to 19A with everything on.
Don't really know what to make of it. I almost made the 1/2 hr drive to town to exchange the GFI breaker for another. Bad breakers aren't unheard of, but aren't all that common either.
What would cause it to trip like that? %99.99999 sure it was not a overload trip.
The unit itself required 2 hots and a grnd.
The disconnect was a CH 50A 2pole GFI Nema 3R
Ran 2 hots a neutral and a grnd to the disconnect.
Ran 2 hots and a grnd to the unit.
Separate neutral (isolated) and ground ( to chassis) bars in the disconnect. Treated them as you would a sub panel ( kept them separate )
The GFI disconnect kept tripping sometimes within a few seconds and sometimes after a minute or so. Then it held and only tripped when I hit the test button.
Had the hot tub on maximum settings the whole time. ( full of cold water, so it was heating )
Current draw was 41A peak for just long enough to read it and then dropped to 19A with everything on.
Don't really know what to make of it. I almost made the 1/2 hr drive to town to exchange the GFI breaker for another. Bad breakers aren't unheard of, but aren't all that common either.
What would cause it to trip like that? %99.99999 sure it was not a overload trip.