Okay here is the is the issue. Within the courtyard of a resort hotel there are about two hundred 277 volt Ballard fixtures. There are 12 circuits run to a 12 pole contactor. Three of these circuits are bad with a direct short causing the main 2000A 480 volt GFIC breaker to shutdown. Through a process of elimination I was able to locate the problem and make the repairs and all lights are back up. With the tripping of the 2000A breaker this resulted any many issues within the resort hotel. The 277/480 sub panel I found 3 tripped breakers. When each breaker in thrown individually each breaker will trip without tripping the main 2000A breaker as it should, but because and I believe when the short occurred I think 480 volts was involved this is why the 2000A blew.
My question and I have not run across this in a lighting situation. The resort is requesting that all ground lighting be placed on GFI's. Can all three phases share the same neutral or will a separate neutral be needed for each circuit.
My question and I have not run across this in a lighting situation. The resort is requesting that all ground lighting be placed on GFI's. Can all three phases share the same neutral or will a separate neutral be needed for each circuit.