Hi, I hope this is the right place to ask this...
At our current residential construction project, the electric power company utilizes a split-phase 230V system without supplying a neutral wire to the building (only two wires). We are requesting a GFI breaker installation from our electrician, but these are still uncommon in this part of the country. That's why I wanted to ask those in the forum who are familiar with these kind of installations, if our system would work correctly? - Specifically, will the GFI still function without a neutral connector?
My father, who is an electronics engineer was concerned about the unclear grounding configuration, since the 8kV transformer is grounded 200 ft away from us, and this neutral wire will not be connected to the ground connector of the building. Do you expect any problems with this?
I'd appreciate any help with this question,
Peter
Here some additional information:
The electrical plan for the building is based on Philippine Electrical Code, which is based on the National Electrical Code of the US. The power distribution is similar to this diagram:
SPECS:
The transformer supplying the building looks like this:
At our current residential construction project, the electric power company utilizes a split-phase 230V system without supplying a neutral wire to the building (only two wires). We are requesting a GFI breaker installation from our electrician, but these are still uncommon in this part of the country. That's why I wanted to ask those in the forum who are familiar with these kind of installations, if our system would work correctly? - Specifically, will the GFI still function without a neutral connector?
My father, who is an electronics engineer was concerned about the unclear grounding configuration, since the 8kV transformer is grounded 200 ft away from us, and this neutral wire will not be connected to the ground connector of the building. Do you expect any problems with this?
I'd appreciate any help with this question,
Peter
Here some additional information:
The electrical plan for the building is based on Philippine Electrical Code, which is based on the National Electrical Code of the US. The power distribution is similar to this diagram:
SPECS:
- primary voltage: 8kV
- primary Neutral (below Phase): one side of primary connected to 1/2" GI grounding rod 8 ft in soil (below electric post)
- secondary 230V between two main output wires (115V towards ground)
- secondary Neutral (in center): connected to same grounding rod below electric post
- secondary two output wires connected to building 200 ft up the street
- neutral wire is not connected to building, but termintes at post across the street
- building has its own ground connection (40 ft concrete encased electrode in foundation ground beam welded to footing rebars)
The transformer supplying the building looks like this: