K kenjunior Member Oct 6, 2004 #1 Ok, I understand everything is supposed to be GFI'd in the commercial kitchen. But (the famous BUT), what about a 30 amp 110 twist lock outlet? Does it need to be on a GFI breaker? Thanks for all the WONDERFUL reading in this forum. kj
Ok, I understand everything is supposed to be GFI'd in the commercial kitchen. But (the famous BUT), what about a 30 amp 110 twist lock outlet? Does it need to be on a GFI breaker? Thanks for all the WONDERFUL reading in this forum. kj
B bill addiss Senior Member Oct 6, 2004 #2 Re: GFI in commercial Kitchen ? Ken, Look at 210.8(B): It says ... all 125v, single-phase, 15- and 20-ampere receptacles .... Bill
Re: GFI in commercial Kitchen ? Ken, Look at 210.8(B): It says ... all 125v, single-phase, 15- and 20-ampere receptacles .... Bill
K kenjunior Member Oct 6, 2004 #3 Re: GFI in commercial Kitchen ? I am working with NEC2002 codes. That is the way I read it too.